alsiuw928als93la
- United States
A company we have contracted is in the process of building a 100 amp motor starter control panel for a heavy industrial plant. The motors are 3 phase 480 vac 5 HP with 1-2 higher HP (20-40 HP). The other components in the panel are 24 VDC PLC I/O for the motors to connect motor current transmitters, motor contactor coils and auxiliary contacts, overload relays, MCP/MPCB auxiliary contacts, and misc cabinet connections.
There are some questions on grounding the motors. In the current panel, the motor grounds are supposed to go to a ground terminal block (that connects to the DIN rail). The ground terminal block is on aluminum DIN rail and it is screwed into the white painted back panel. I do not believe any paint has been etched off on the DIN rail. There is no extra screw dedicated for earth on this DIN rail. There is no wire bonding of the DIN rail to the AC ground. The AC ground is connected at another point in the panel at a dedicated ground point.
The ground for the motors is therefore expected to travel through the ground terminal block on the DIN rail, through the screw on the DIN rail, through the back panel to the AC ground. Aesthetically it is a nice solution but I'm not sure on functionality or side effects. I have tried to dig up past articles, but a lot of grounding questions were tied to lower voltage/lower amperage panels. It was harder to find this scenario with motor panels.
a) Would you find this acceptable?
I have read a forum post that suggested aluminum wasn't acceptable, but steel was. I had a hard time trying to find documentation on this. I also read where an inspector required a separate screw for the ground on the DIN rail as well as requiring a separate bonding cable from the DIN rail to the primary AC ground screw.
b) If the DIN rail/screw/back panel ground is acceptable for 480 vac, can the 24 VDC components be ruined because of this? Let's say there is a fault, could I make a bad thing even worse by frying all of the 24 VDC? What if there wasn't a large fault but a small fault where there is a small amount of current.
c) Last of all, is there a common convention? For example, even if the above is acceptable, would you do something else and what would that be?
Thank you!
Thank you!