The 2005 NEC of NFPA 70 has added section 409, Industrial Control Panels and identifies the requirement to mark such a panel with the short circuit current rating (SCCR).
Reference to one approved method of calculating it that of Supplement SB of UL 508A.
What I find out is that following the Supplement SB of UL508A results in identifying most panels with a 5ka SCCR vaule.
If you have a panel requireing a 200A service and rating at 5ka SCCR--How can you supply power to this panel?
Anyone have issue with this?