Perhaps someone can post Charlie’s rule, I don’t have a copy with me.
I found it and read it. Basically it sounds like you're saying if it's not in the code it's "Legal", but if OSHA decides it's not in this particular instance than it's up to them to decide....?Perhaps someone can post Charlie’s rule, I don’t have a copy with me.
Or I'm interpreting it wrong. I don't even understand anymore after reading itPerhaps someone can post Charlie’s rule, I don’t have a copy with me.
I don't believe you can just "call" OSHA and ask for such a decree. You can ask for it in writing though.So what your saying is, if I call OSHA and they say, "it's not okay", it's then "Not okay" because they write the fine?
You can call and ask. They'll give you their "best" answer, but ultimately you need to file a complaint for them to inspect and make a final interpretation based on all the specific details of the particular equipment. I just got off the phone with OSHA and they said, just based on hearing it, if a panel is blocked and something needs to be moved (on wheels or not) in order to "shut off or maintenance" of electrical equipment, it sounds like it's at the least an OSHA violation as electricians need access for emergency circumstances. If I read "Charlie's rule" correctly based on the posts I've read, The statement was made, "If there is no direct code specifying something, it's then not in the code". So what IS specifically in the NFPA 79 is direct working space clearances for electrical equipment on industrial equipment. Nowhere does it state wheels make it exempt. Looking at it from a clear "newbie" first time reading it, that's what I'd assume too. If I'm missing something, please let me know. I'm looking for clear guides as to what IS in the code now that would specify it in better/more detail.I don't believe you can just "call" OSHA and ask for such a decree. You can ask for it in writing though.
It does say by definition that an "Industrial machine" is something that's "Not portable by hand while working". This is the only thing to me in question.You can call and ask. They'll give you their "best" answer, but ultimately you need to file a complaint for them to inspect and make a final interpretation based on all the specific details of the particular equipment. I just got off the phone with OSHA and they said, just based on hearing it, if a panel is blocked and something needs to be moved (on wheels or not) in order to "shut off or maintenance" of electrical equipment, it sounds like it's at the least an OSHA violation as electricians need access for emergency circumstances. If I read "Charlie's rule" correctly based on the posts I've read, The statement was made, "If there is no direct code specifying something, it's then not in the code". So what IS specifically in the NFPA 79 is direct working space clearances for electrical equipment on industrial equipment. Nowhere does it state wheels make it exempt. Looking at it from a clear "newbie" first time reading it, that's what I'd assume too. If I'm missing something, please let me know. I'm looking for clear guides as to what IS in the code now that would specify it in better/more detail.
Show me a rule that specifically addresses work space requirements for cord and plug connected equipment.They have a specific section for "Industrial machinery" in the NEC which states...."For further information, see NFPA 79" or "For information on the workspace requirements for machine power and control equipment, see NFPA 79" . The NEC tells you to look there for those specific code requirements which list close to the same requirements as the NEC for workspace (besides a lot of the lower voltage control equipment. If we ignore the NEC for industrial equipment, we ignore the NFPA.
Show me a place where...Show me a rule that specifically addresses work space requirements for cord and plug connected equipment.
So do you need to provide clearance, per 110.26, for a submersible pump? How about for a fan motor internal to an air handler?Show me a place where...
"II. 600 Volts, Nominal, or Less 110.26 Spaces About Electrical Equipment. Access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment."
is invalidated just because it's on a cord or plug.
So do you need to provide clearance, per 110.26, for a submersible pump? How about for a fan motor internal to an air handler?
In my opinion if the device is being maintained while energized, 110.26 clearances are needed. If all maintenance occurs while the cord is unplugged, those clearances are not required.
There is exceptions for particular equipment having specified workspace exemptions like
"620.5 Working Clearances. Working space shall be provided about controllers, disconnecting means, and other electrical equipment in accordance with 110.26(A). Where conditions of maintenance and supervision ensure that only qualified persons examine, adjust, service, and maintain the equipment, the clearance requirements of 110.26(A) shall not be required where any of the conditions in 620.5(A) through (D) are met.
Which is for any of the items listed in 620, but I see nothing but more defined clearances for industrial equipment through the NFPA 79.
I'd guess submersible pumps are designed and meant to be submerged so I'm completely unsure how that one would work at all.