Industrial Lighting

Status
Not open for further replies.
I am wondering if a common neutral can be used for more than one circuit, if the size of the neutral will hold the amperage of the shared circuits. IE: three 20 amp circuits using a common #6, and will this meet code? New to this site but I love the Q&A. Thanks
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
What you are addressing is called a "multi-wire branch circuit," and it is allowed under NEC article 210.4. But there are restrictions that you need to understand, so I suggest reading it carefully. Also, if the three circuits originate from three different phases of a 3-phase panelboard, then the current in the neutral is likely to be far less than the current in any of the phases. Unless the lights are of a type that brings a lot of harmonics into play, you can use a #12 for the neutral.
 
Thanks for the quick reply and info. I was refering to 225.7 (B) in that one neutral for each phase. The question my colleges and myself have is if that one neutral could be shared if sized according to the ampacity of other circuits. I thank you guys for your answers, the code is sometimes hard for me to interpret.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thanks for the quick reply and info. I was refering to 225.7 (B) in that one neutral for each phase. The question my colleges and myself have is if that one neutral could be shared if sized according to the ampacity of other circuits. I thank you guys for your answers, the code is sometimes hard for me to interpret.


That Article only applies to outside installations:

ARTICLE 225 Outside Branch Circuits and Feeders
225.1 Scope.
This article covers requirements for outside branch circuits and feeders run on or between buildings, structures, or poles on the premises; and electrical equipment and wiring for the supply of utilization equipment that is located on or attached to the outside of buildings, structures, or poles.
 