Industrical manufacturing building

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Does anyone know which code cover electrical installation for manufacturing building (480V or less), NEC article 545 seems does not have much detailed content. Thank you.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
are you asking about a manufactured building similar to a mobile home ???
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Assuming its a factory, it would be pretty much standard stuff - no particular code requirements I can think of stand out.

In factories, it usually more what their staff engineers and maintenance people want.

If they are hard core, you might have dual ended substations, bus ducts running through every bay, rigid steel conduit for extra protection, and some column width panels.

General use receptacles are usually few and far between, unless needed for specific equipment.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If there is any sort of hazardous / flammable process taking place, there is a lot more to consider. Without knowing what you mean by "manufacturing building", we can't help.
 

Fnewman

Senior Member
Location
Dublin, GA
Occupation
Sr. Electrical Engineering Manager at Larson Engineering
Generally, all portions of the NEC not specifically addressing residences or other structures, would apply. In practice, large industrial plants and their design engineers make most of the code interpretations as there is often no AHJ capable of addressing projects of such large scope.
 

kwired

Electron manager
Location
NE Nebraska
Too many possibilities of what kind of things you may run into in a manufacturing plant.

Specific types of activities that occur may lead you to specific areas of the NEC. If you have flammable gases or combustible dusts present on a usual basis, you will see a lot of the hazardous location sections in chapter 5.

Motors are usually common in manufacturing, so you probably get to use art 430 frequently as well.

If you have a full time maintenance staff that has "qualified individuals" that are the only ones that do electrical maintenance and operations - you may be able to use the exceptions/options here and there in the code that usually start with "where qualified individuals....."
 