Tulsa Electrician
- Tulsa
- Electrician
So the cu rated wire but is good for copper clad.
I'd have to research it, but I think all wire nuts are so listed.I'm reading 110.14 2014 NEC.
Will see if any change in 2017.
I do not have a 2020 to see if change is made.
The way I read it the wire nut in this case would need to be "identified for purpose and condition of use". For copper to copper clad.
Yes, first I was going to say that of course you can use any copper device/termination with CCAL, as the contact surfaces are copper. But then I started to wonder whether the connection design has to take into account the thermal expansion coefficient, as presumably for CCAL that's closer to Al than Cu, and they differ (ratio of 23/16).One of the proponents arguments for copper clad AL is that you can use standard devices, wire nuts, etc.
Price for me isCan some post the cost for CCA and CU romex in 250 ft rolls?
Good point. It'd be fun stuffing a box with two #10 cables and a GFCI.I also was looking at box fill using #10 copper clad. I can see some installation practices need to be adjusted.
I've seen that in a 14 cu. in. boxGood point. It'd be fun stuffing a box with two #10 cables and a GFCI.![]()
Yes, box fill is already an issue with many ill informed electricians. There will need to be an adjustment in the everyday electricians thinking if CCA is going to be a thing as I suspect it will.Good point. It'd be fun stuffing a box with two #10 cables and a GFCI.![]()
I think...So I have access to copper clad nmb.
Have not used much but what little I have I liked.
I want to wire a house in this. Would you inform owner. Or not worry.
I don’t think it’s is an issue, though I might be thinking with my pocket book.
While the wiring devices are fine, the standard wirenuts are not listed for use with copper-clad aluminum.One of the proponents arguments for copper clad AL is that you can use standard devices, wire nuts, etc.
And the GFCI probably doesn't accept 10 AWG conductor so you will need some additional connectors and 12 AWG pigtails to take up more room in the box.Good point. It'd be fun stuffing a box with two #10 cables and a GFCI.![]()
I thought the same thingAnd the GFCI probably doesn't accept 10 AWG conductor so you will need some additional connectors and 12 AWG pigtails to take up more room in the box.