jwelectric --I am not sure what you mean by no seal in a deck box for a pool light stop air infiltration.

and about 430.83

what about the motor controller. how do you prevent power to the time clock to service. if breaker is out of sight. I have heard about homeowners turning the power back on by mistake and shocking the electrician.
 
430.102 states that a disconnect shall be insight of the controller and motor.

If this clock has a switch that disconnects all ungrounded conductors that is with-in sight of the clock and motor then you have fulfilled the code requirement of the disconnect.

Personally I don?t see the time clock as a motor controller but a device to control the circuit.

430.83 states that a switch can be the disconnect for the motor
 
jwelectric said:
430.102 states that a disconnect shall be insight of the controller and motor.

If this clock has a switch that disconnects all ungrounded conductors that is with-in sight of the clock and motor then you have fulfilled the code requirement of the disconnect.

It disconnects the motor for the pool but not the time it self of feed to.
I have seen some pretty bad things like while working on items like this the HO would help by turning on breaker.Buzzzzz
Personally I don?t see the time clock as a motor controller but a device to control the circuit.

430.83 states that a switch can be the disconnect for the motor

A device that turns on a motor and off at a predetermined intervals
 
Mike,
If this clock has a switch that disconnects all ungrounded conductors that is with-in sight of the clock and motor then you have fulfilled the code requirement of the disconnect.
I don't think so...look at 430.109.
Don
 
430.109 (C) Stationary Motors of 2 Horsepower or Less For stationary motors rated at 2 hp or less and 300 volts or less, the disconnecting means shall be permitted to be one of the devices specified in (1), (2), or (3):
(1) A general-use switch having an ampere rating not less than twice the full-load current rating of the motor
(2) On ac circuits, a general-use snap switch suitable only for use on ac (not general-use ac?dc snap switches) where the motor full-load current rating is not more than 80 percent of the ampere rating of the switch
(3) A listed manual motor controller having a horsepower rating not less than the rating of the motor and marked ``Suitable as Motor Disconnect''

Why can a switch not work?
:)
 