I have inherited a job that will be incorporating up to a 15kw system, largest allowed by our utility. There is a 320 meter socket with (2) 200 ge disconnects, disconnects are single breaker enclosure so no busbars, this is already installed. Meter pedestal is approx 200' away from barn, and 300' away from where we will likely enter the residence. Load calcs have not been done on the house, but I could foresee taking 300 amps to the residence, large residence, multiple dryers, the chance for a electric car or two. My initial plan was to send two feeders to the house ( local ahj has approved with placards posted at service location and house location). One of the 200 disconnects to feed the house and the other 200 to feed a 100 to the house and 100 to the barn, utilizing the outside feeder tap rules and terminating in 100 amp over-current devices at the appropriate structures. Solar panels will be mounted on barn roof and fed into the barn panel, 150 amp bus with 100 amp breaker, this would allow the solar company to feed with the max size of 80. Now to my sticking point, there is already a 200 breaker installed at remote meter pedestal, what rule would come into play since I have no busing in this enclosure, just the breaker lugs? Would I need to remove the 200 amp disconnect and install a 400 to give me the 80 amps for the solar?