How can I calculate/determine if the 100A circuit breaker protecting a transformer won't trip due to inrush current?
I have a transformer rated for 25KVA
Primary: Operating on 208V single phase using 2 wires
Secondary: Operating on 480V single phase using 2 wires
The connected load on the secondary is 13300 VA operating at 480V single phase.
Per Per NEC Table 450.3 B Primary protection only: the maximum primary protection is 120 * 1.25 = 150A.
However, the existing panel has a label stating to use 100 A circuit breakers maximum.
How can I guarantee a 2-pole 100A breaker on the primary side won't trip due to inrush current?
Are their any calculations I can perform?
Should I use an HACR breaker?