May I assume that you are tripping the MCP? If so has the MCP been sized and set per NEC art 430-152? K3p in mind that the term " inrush" should not be confused with the motors locker rotor current but as one of the other posters brought up is the peak current the occurs when the motor is first energized which most meters are incapable of capturing the value. This current may reach 13x the FLAs for energy efficient motors. Motors commonly today are energy efficient which equates to a much higher than the average motors in the past.A client has a bank of 3 motors that keep tripping on start. We took the trouble to measure the actual values, and it's no wonder why they keep tripping, but we can't understand why the inrush is so high. We were thinking of just adding soft starts and calling it good, but we want to understand what the problem might be first. Please see the attached PDF "inrush". The values in the red squares are nearly 200A for 7.5HP motors, and the running current is only about 4A, which is normal. What could be causing such a high inrush? The motor KVA code is K, not V so this is not a "feature" (see attachhed PDF "motor data").
Any ideas?
MCPs are mag (instantaneous) only devices that protect the motor circuit should the motor fail, a failure cause by a winding to ground fault and winding to winding fault. Should the mag setting of the MCP be set to low the inrush (magnetizing) current most likely will nuisance trip the on start up. My recommendation is to become familiar with NEC art 430-152 and set the MCP at the highest setting that is allowed. Remember that if you feel uncomfortable with that setting you can keep tweeking the setting down to a point just above where you would get nuisance trips.
You will note the NEC art 430-152 refers to the MCP as ground fault protection.
What hasn't been included by the OP is what the MCP is and what available settings are available and where the MCP is set.
MCPs come from the factory set in the lowest position and the tech. must then readjust that setting per NEC art 430-152. While as an applications engineer I had received countless question regarding nuisance tripping MCPs when they were not set properly.
Now, it may be that the OP is referring to an OLR trip which is thermal. Then you take s look at what may me causing excessive current during start up after assuring that the proper heaters have been installed or if adjustable adjusted correctly. Should there be something during startup that caused the LRA to bwe long enough the OLR would trip to protect the motor winding from being damaged by excessive heating. If this thern is the issue it would now be appropriate to investigate the driven load.