cschmid said:
Now I am going to stir the pot here....
OK....your choice. :grin:
Just for the record I do not do multi wired branch circuits and have a dislike for them...
Electrically they behave like every service or feeder that you have ever worked with.
I have seen where you could weld the inside of the outlet off and not trip the double pole breaker.
Yes, and I have seen it with single pole breakers.
Can you think of any electrical reason why the breaker would behave differently?
..I have seen 240V heaters added to the circuit cause it is on a double pole.
And that is a problem?
The NEC allows supplying both 120 and 240 volt loads with one circuit.
Happens all the time with electric ranges, electric dryers, services and feeders.
we recently rewired an entire commercial kitchen that was MWB...the circuit breaker failed to trip and toasted a 5k Stainless frig..
I doubt that MWBC was the actual problem, there may well have been miss-wiring.
I have no time for MWB as long as 2 pole breakers are used and not handle ties...
No time....

MWBCs save me time and money, they also use less copper. Many times a MWBC will waste less power due to voltage drop.
and can any tell me why using handle ties you would have a safer operation than on a two pole breaker?
One circuits failure will not take out one or two more circuits.
I have seen many fail and at the cost to the customer but yet where handle ties are used less failure...I am clueless here, I thought the 2 pole breaker worked the same as a single pole....
They do work the same. Maybe just the luck of the draw you ran into some bad ones.
When I get prints the first thing I will do if allowed by job specs is layout as many 3 circuit net work home runs as I can, they are simply more efficient and make a huge difference with the number of current carrying conductors in a raceway resulting in much less derating then all two wire circuits would require.