dnem said:If singles are used with handle ties, the circuit that trips won't kill the other circuits.
David
That is how the theory is supposed to work...
dnem said:If singles are used with handle ties, the circuit that trips won't kill the other circuits.
David
ryan_618 said:That is how the theory is supposed to work...
cschmid said:I think MWBC were designed to save money on circuits that have small to no load on the neutral. The modern day lighting loads are increasing in neutral loads.
When a small expansion takes place all new pipe and circuits are now needed.
Unqualified maintenance personnel and home owners are not very knowledgeable on MWBC
the down side has more consequences than the up side.
dnem said:I'll bet that more times than not, all of the panels handle ties disappear right after the the first time one of those breakers trip and take out 2 or 3 circuits
iwire said:Who is removing handle ties?
I have been at this 25 years and I can't recall finding removed handle ties or ever considering removing existing handle ties.
roger said:reduces voltage drop, reduces wattage used
Roger
SmithBuilt said:How does it do those things?
SmithBuilt said:How does it do those things?
cschmid said:Al-thought and also have seen them sorted to be on the same phase so no handle tie could be used...
cschmid said:One of the reasons I feel that money is saved on not installing MWBC is that I can stagger the lighting schemes and work on de-energized circuits during regular hours and not shut down the business...
cschmid said:I do not install maxed out piping I have room to spare for expansion what is the difference between hundred feet of 3/4" vs 1/2" installation cost are the same except when we go to expand we save owner cash no need to run a bunch of extra pipe.
This doesn't make sense. Why would more than one breaker be affected?cschmid said:The benefits of not using MWBC in commercial and industrial out way the cash benefit of installing up front. when you count extra cost for off hour work and lost production when A ballast shorts out and shuts down a line because you lost two or three banks of lights instead of one. We do not have to work live circuits and do not have to do work after business hours this saves us money and our client money.
cschmid said:We can not idiot proof the world but I know unqualified people are going to do electrical work and I do care they have families too. I don't agree that they do the work but I can not stop them. We live in the same community, we know these people outside of work and our kids might of played together they might even be married to someone I know. WE do care it is our community together we make it work.
cschmid said:The benefits of not using MWBC in commercial and industrial out way the cash benefit of installing up front. when you count extra cost for off hour work and lost production when A ballast shorts out and shuts down a line because you lost two or three banks of lights instead of one. We do not have to work live circuits and do not have to do work after business hours this saves us money and our client money.
I think the way the arrows are drawn isn't quite right, IMO. I think of it as two hots feeding in, and the neutral returning the unbalanced portion. Ed's drawing may be correct and I'm off base, but I can't understand the arrows as drawn.SmithBuilt said:In diagram B why would current that has gone thru load #1 then go thru load 2 and not take the easier path of the neutral wire?
SmithBuilt said:In diagram B why would current that has gone thru load #1 then go thru load 2 and not take the easier path of the neutral wire?
iwire said:Who is removing handle ties?
I have been at this 25 years and I can't recall finding removed handle ties or ever considering removing existing handle ties.
SmithBuilt said:The only downside that I see is that there will be more pressure to do live work. Instead of turning off 1 circuit you may have to cut off 2 or 3. Especially in businesses.
The upside to that is the neutral shouldn't have voltage on it.
augie47 said:I have a decade or two on you, Bob, and I agree. I have rarely seen the ties removed, and in those few cases, that was the least of the electrical problems.
cschmid said:We can not idiot proof the world but I know unqualified people are going to do electrical work and I do care they have families too. I don't agree that they do the work but I can not stop them. We live in the same community, we know these people outside of work and our kids might of played together they might even be married to someone I know. WE do care it is our community together we make it work.
dnem said:I see it as a potential code requirement but I don?t see it as a safety hazard or a problem. . At least not a hazard for a real electrician.
The code panel must be viewing it as a safety hazard for untrained workers but I see it as a government abdication of responsibility.