KnobnTube
Contractor friend asked me if I had any input on the situation.
Inspector did not give Article but failed inspection until correction is done.
I have no idea.
There is a MWBC to separate receptacles.
Room with MWBC is merely a bonus room, so no particular need on amperage.
Older home getting a service upgrade.
The MWBC is question has one receptacle on a 15 amp and the other is 20 amp.
So, we have 15 and 20 amp breakers tied together with proper handle tie.
Neutral is #12, then the #14 and #12 on the breakers.
Inspector says "no", the #14 must be changed to #12 and both breakers must be 20 amp.
He did not leave any additional information as yet.
Thought would post and see if anyone had any ideas before he confronts the inspector, as we cannot find anything stating they must be the same, as long as the neutral is equal to the highest amperage breaker.
Ideas?
Thanks
I have no idea.
Ideas?
Thanks