Inspector change

Status
Not open for further replies.
Hi, I recently ran into a problem with an inspector. I had 2x2 flourescent fixtures mounted in a suspended ceiling. They were cord and plug connected above the ceiling with a 14 gauge SJT cable. The ceiling is a plenum ceiling. The inspector told me I could not do this. Why? I thought SJT was rated for plenum.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The inspector is correct, see Table 400.4 and 400.8(5)

Roger
 

haskindm

Senior Member
Location
Maryland
The Inspector has it right. You may install a receptacle above a drop ceiling, but you may not plug a flexible cord into it. Kind of a Catch-22 isn't it?
 

iwire

Moderator
Staff member
Location
Massachusetts
What is a wall wart?

Plug in transformer

transformer.jpg
 