Inspector change

Status
Not open for further replies.
Hi, I recently ran into a problem with an inspector. I had 2x2 flourescent fixtures mounted in a suspended ceiling. They were cord and plug connected above the ceiling with a 14 gauge SJT cable. The ceiling is a plenum ceiling. The inspector told me I could not do this. Why? I thought SJT was rated for plenum.
 
The inspector is correct, see Table 400.4 and 400.8(5)

Roger
 
The Inspector has it right. You may install a receptacle above a drop ceiling, but you may not plug a flexible cord into it. Kind of a Catch-22 isn't it?
 
What is a wall wart?

Plug in transformer