Yes, that too!The picture does not show the NM path. Is it installed above a drop ceiling ??
334.12 Uses Not Permitted.Yes, that too
Agreed, never Romex, MC or pipe it.I hate to be a snob, but. I just don't do romex in commercial. Let someone else do that.
Same here, but most of my competitors are resi guys. Other than chain stores, most commercial around here is built like a house, Sheetrock ceilings and all. I still have a lot of customers that want it done right. There was a plumber in the supply house the other day that was wanting to put up nuclear exit signs in a restaurant that was built like that, not because the city wanted them, but because the insurance company wanted exit signs.I hate to be a snob, but. I just don't do romex in commercial. Let someone else do that.
In many of my local areas ( no state license ) starting st least back to the 1980's you were not allowed to use type MC cable outside of one & two family dwellings.One township did not allow type AC ( Ya BX ) in industrial or commercial sites. Had to go with MC cable.I hate to be a snob, but. I just don't do romex in commercial. Let someone else do that.
But it is nice and flat and straight!This is in a convenience store next to the coolers. Does anyone see a problem with this? I am secured within 12" of the box and every 48" just to be safe. Yes, this is a public area, but I don't think it's subject to physical damage.
View attachment 2579487
Are you saying that would be okay if it was residential?Definitely needs to be in a wall because it is not residential. Ditto on being above ceiling.
Eh... I could be persuaded on the subject to physical damage portion. NM is permitted to be run exposed, so unless I see an actual hazard that could damage the wiring, I could be ok with it kinda tucked in a corner out of the way like that. Close call for me. I am an anomaly in the inspection industry for my liberality on that subject.Are you saying that would be okay if it was residential?
Would you allow it to be painted? Or would that be a violation of 310.8.Eh... I could be persuaded on the subject to physical damage portion. NM is permitted to be run exposed, so unless I see an actual hazard that could damage the wiring, I could be ok with it kinda tucked in a corner out of the way like that. Close call for me. I am an anomaly in the inspection industry for my liberality on that subject.
Also just to add to the 334.10(3) reference I don't think NM cable is permitted in any type II construction justI would assume 334.10(3), requiring cables to be within walls.