Helped out a friend with a service change the other day. He had it inspected today. A few things the inspector wanted, agree? Disagree?
I know what I think...discuss!
1. #4 Cu must go to the neutral bar where the neutral is connected not the bar on the opposite side of the panel. "What if the bonding screw comes loose, you will lose your ground, you can't rely on just that screw"...."
"Just jump the two bars with a #6 and you're good"
2. Install GFCI receptacle at panel. Or "if you want to use the existing basement receptacles to count as the "Required receptacle" you have to change them to GFCI."
3. GEC has to connect to the street side of the meter. "I'll make it easy for you, just add a jumper around the meter and you'll be ok"
The GEC hit the pipe within 5' of entry and jumped across water meter already.
Also he mentioned that since the new AFCI requirements guys are installing fewer circuits in new homes. He will be checking to make sure you install as many circuits as the code requires.
I know what I think...discuss!
1. #4 Cu must go to the neutral bar where the neutral is connected not the bar on the opposite side of the panel. "What if the bonding screw comes loose, you will lose your ground, you can't rely on just that screw"...."
"Just jump the two bars with a #6 and you're good"
2. Install GFCI receptacle at panel. Or "if you want to use the existing basement receptacles to count as the "Required receptacle" you have to change them to GFCI."
3. GEC has to connect to the street side of the meter. "I'll make it easy for you, just add a jumper around the meter and you'll be ok"
The GEC hit the pipe within 5' of entry and jumped across water meter already.
Also he mentioned that since the new AFCI requirements guys are installing fewer circuits in new homes. He will be checking to make sure you install as many circuits as the code requires.