UNLESS, of course, someone is working in the energized panel. Then there is a likelihood of occurrence of an arc flash event, so anyone within the arc flash boundary would need to be suited with the appropriate PPE.Not true guys. Opening up the panel is when you need to wear PPE. After that you just need to keep folks out of the limited approach boundary (LAB) which is 42" for under 151-750V. They can even cross into the LAB if escorted by a qualified person. That's how IR scanners can get as close as the Restricted Approach Boundary without wearing PPE, because there's no likelihood of occurrence of an arc flash incident per table 130.5(C).
I was referencing the case where the panel is open but there is no activity going on with it.