• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Inspector question

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
Re: Inspector question

Originally posted by a.wayne3@verizon.net:
OK what if like I did a few years ago have a home,192 ft from the panel to the closest wall in the master BR.Owner wanted all panels in the garage 600 amp single phase service.
Just a small place :D

[ February 21, 2004, 06:31 AM: Message edited by: iwire ]
 

highkvoltage

Senior Member
Re: Inspector question

Mr.Walker. I believe you hit the nail on the head. The inspector didn't turn him down for using the 15 amp breaker he was probly turned down because the circuit was required to be 20 amp. Here they require the kitchen counter receptacles to be on a 20 amp circuit. They would not approve if I installed 12/2 then landed on a 15 amp CB. Reguardless of my wire size it's now a 15 amp circuit.
 
Status
Not open for further replies.
Top