Do you all think that the requierment of 210.52(E)(1) allows the receptacles required @ front & back of the dwelling, accessible from grade if you have to go up 3-5 steps to a porch or deck?
Do you all think that the requierment of 210.52(E)(1) allows the receptacles required @ front & back of the dwelling, accessible from grade if you have to go up 3-5 steps to a porch or deck?
Do you all think that the requierment of 210.52(E)(1) allows the receptacles required @ front & back of the dwelling, accessible from grade if you have to go up 3-5 steps to a porch or deck?
For a front porch with 3 steps we do that all the time. At the rear of the home with a wood
deck is the w/p recptacle reachable from grade ? If so good to go. If not accessible then add
another one.
From 2008, 210.52(E)3 requires at least one on the porch, but that installation does not relieve one from having to comply with (E)1.
So, you have to have both, one on the porch and one in the front and back accessible while standing at grade level.
(E) Outdoor Outlets. Outdoor receptacle outlets shall be
installed in accordance with (E)(1) through (E)(3). [See
210.8(A)(3).]
(1) One-Family and Two-Family Dwellings. For a onefamily
dwelling and each unit of a two-family dwelling that
is at grade level, at least one receptacle outlet accessible
while standing at grade level and located not more than
2.0 m (61⁄2 ft) above grade shall be installed at the front and
back of the dwelling.
Do you all think that the requierment of 210.52(E)(1) allows the receptacles required @ front & back of the dwelling, accessible from grade if you have to go up 3-5 steps to a porch or deck?
(3) Balconies, Decks, and Porches. Balconies, decks, and
porches that are accessible from inside the dwelling unit
shall have at least one receptacle outlet installed within the
perimeter of the balcony, deck, or porch. The receptacle
shall not be located more than 2.0 m (61⁄2 ft) above the
balcony, deck, or porch surface.
Do you all think that the requierment of 210.52(E)(1) allows the receptacles required @ front & back of the dwelling, accessible from grade if you have to go up 3-5 steps to a porch or deck?
I don't buy that because the receptacle will still below the 6 1/2 feet above grade.
So, you can install 6.5' above grade, which maybe at deck level, and still pass. Walking up 3 steps over to it, does not make it accessible while standing at grade level.
Do you all think that the requierment of 210.52(E)(1) allows the receptacles required @ front & back of the dwelling, accessible from grade if you have to go up 3-5 steps to a porch or deck?
But it still has to be accessible, see below.