I wanted to know what some of the inspectors here think of a couple of things I have been "called on" in the past.
And here is another tricky one, typically in res work I use a 7/8 bit. I see no problem with say... three 14/2's and two 14/3's in the same hole, it was not hard for me to get the nm in there and each wire can move relatively freely when tugged upon, yet I have had inspectors that think otherwise.
Opinions?
300.17 Number and Size of Conductors in Raceways.
The number and size of conductors in any raceway shall not be more than will permit dissipation of the heat and ready installation or withdrawal of the conductors without damage to the conductors or to their insulation.
I know this section does not pertain to cables in bored holes.
I use it as guidance for making decisions on how many cables can be pulled through bored holes.
There is no restriction in the NEC as to how many cables can be installed in a bored hole.
Some judgement has to be used in the installation, such as damaging the cables during installation.
I know a lot of people including inspectors who will limit the number of cables to 3....where is that stated in the NEC.
Anyone who uses the derating argument also has no basis in the NEC for that argument.
Remember part of the requirement/restriction of ampacity adjustment.
"...where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 24in. and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as..."
There is no definition or measurement specified in the NEC in regards to spacing. It does not take much spacing for the cables to be able to dissipate heat when not installed in a raceway.
Pulling multiple cables through bored holes can be acheived without ampacity adjustment, some prudence should be observed though.