I have been working on a custom home and called for a rough for today. First mistake...I wasn't there. Inspector failed the job because I used wire nuts to splice my EGCs. He cited 110.2 and scribbled a note that said that wire nuts are not listed or labled for grounding. I have changed everything to compression sleeves (Buchanons) and called for a reinspection. After 35+ years in this business am I learning something new or is the inspector one fry short of a Happy Meal. In commercial/industrial, that's all I ever use and no one has said a thing. I welcome any input.
Thanks
Mike
Thanks
Mike