Been thrown a curve ball and I'm second guessing myself.
I had a breaker fail that powers a 150 HP pump located in a NEMA 7 enclosure so of course replacing this is going to be a pain.
What is/was installed is a GE instantaneous 400A breaker set at 2200A. (Breaker adjustable range is 1200-4000A)
Unfortunately the breaker that is currently installed is obsolete but a suppler has a similar that may work. What is recommended is a another GE instantaneous 600A breaker of the same model number (Breaker adjustable range is 1000-3000A )
Does this make sense? My thinking is any size breakers can be used along as the trip setting is with in NEC 430.52?
Thanks