edit to last: Wire is a #3/0 about 15ft away from the starter to the pump.

The enclosure which is fed from a (don't judge) up stream splice box , and another upstream splice box (tapped twice) and finally a 600A 480V breaker off another switch rack which is eventually fed from a 2,000KVA 13.2/480V XFMR. I would say from the source to the breaker about 400'.
size 5 starter

Your 2/0 wire size is fine for 480V, 173A @ 400'. Provided that 2/0 is all the way to the source, and the source voltage is correct/within nominal.

As for the breaker, I would PM zog who's already replied on this thread for a new/remfg/NOS breaker.
 