I got the impression from the original post that the plan was to install a disconnect on a pole at each trailer. That would make them not at the same location and a violation unless there was upstream OCPD.

Maybe the OP meant that the three disconnects would be on the same post.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)

Send this link and pics to you electrician.
Maybe it will help.
That would be the ideal scenario but according to the OPs most recent thread the whole ball game changed.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The only possible problem I see with 3 sets of conductors from transformer is that you would have to use something like a Polaris connector to avoid having two many wires per lug. So the single wire to the lug would have to be large enough to be protected by the sum of the downstream OCPDs.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
That would be the ideal scenario but according to the OPs most recent thread the whole ball game changed.
Thank you.
I'll review.
 