Installation of 2 x 4 ft light fixtures

Status
Not open for further replies.
Re: Installation of 2 x 4 ft light fixtures

In Oregon it is...Slack wires (two) diagonal corners. Screw or factory clip on all four corners to the tee bar.
 
Re: Installation of 2 x 4 ft light fixtures

Thanks, thats what I thought. That answer though is not one of the four multiple choice answers on the test
 
Re: Installation of 2 x 4 ft light fixtures

What test is this? I.M.H.O. siesmic of light fixtures is drvien by the following: IBC 1621.2.5, UBC 25-2, CISCA 3-4, ASCE-7. It depends on the grid system. What is the gauge of the main runners? Is it a heavy duty grid? What siesmic design category or siesmic zone are you in? I don't like that question...not enough info.
 
Re: Installation of 2 x 4 ft light fixtures

Siesmic restraint for drop in troffers is not an NEC issue. the NEC only requires the troffers be secured to the grid...
 