I'm designing a new emergency 3 phase generator for an existing station (please see attached schematic, clouded area). The existing ATS is 3-pole without switched neutral. According to the NEC, this configuration is deemed a non-separately derived system. I've done some studying on grounding of standby power systems but an still questioning my installation.
I have two questions:
1. If the utility has a supply-side bonding jumper, do I need to run the generator neutral or can I simply tie the generator EGC to the ATS EGC as shown in the schematic? In this scenario, it appears the fault current for a line to ground fault would only return to the utility neutral. On the other hand, bonding the generator neutral to the utility neutral in the ATS would allow fault current for a line to ground fault to return back to the generator.
2. Because the installation is not a separately derived system the NEC doesn't require a GEC. However, our utility standard calls for the generator to have a supplementary GEC. Is it better practice to install a separate grounding electrode system for the generator OR connect the generator GEC to the existing electrical enclosure grounding electrode system?
Thanks for the comments.