Installation of Romex in Conduit or Raceway...

Status
Not open for further replies.
In those code references does it say Romex?

BTW if you were answering "yes" to my original question...you are incorrect...
If you use the correct name for "Romex" it's NM cable which is in the section I posted in post #8. As previously stated YES NM cable is permitted in raceways.
 
"Romex" it's NM cable...yes it is, however it is a particular type of NMC that the code does not specifically state or exception to for
Conduit or Raceways!

"As previously stated YES NM cable is permitted in raceways."

Again the correct answer is No...

Lets Start here...

The National Electrical Code (NEC) frequently emphasizes the requirement to use materials that are "listed" (evaluated and approved by a recognized testing laboratory, such as UL) to ensure safety, reliability, and compliance with applicable standards.

One of the most notable references is NEC Article 110.3(B), which states:

"Installation and Use." Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
This means that materials used in electrical installations must not only be listed (tested and approved by a recognized testing organization) but must also be installed according to the manufacturer’s instructions and the conditions of the listing.

Do you agree so far?
 