installing doorbell XFMR in blue box ??

Status
Not open for further replies.

rt66electric

Senior Member
Location
Oklahoma
I was doing a infrared survey and noticed a warm doorbell
upon closer inspection the electrician had installed the doorbell transformer inside a blue carlon box then mounted the doorbell over it.

Is this a legitimate installation??
 

John120/240

Senior Member
Location
Olathe, Kansas
I will say Yes. I have done such installs on a slab foundation. With a Ranch or Two Story the preferred location is in the basement on a Smoke Detector or pull chain. This is just personal preference.
 

JFletcher

Senior Member
Location
Williamsburg, VA
I was doing a infrared survey and noticed a warm doorbell
upon closer inspection the electrician had installed the doorbell transformer inside a blue carlon box then mounted the doorbell over it.

Is this a legitimate installation??

Only thing that comes to mind is that mfg directions/installation may require some working space/clearances.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So you have high voltage and low voltage in the same box? How is the transformer mounted? I doubt this is compliant.
 

tkb

Senior Member
Location
MA
Sounds pretty hack to me.
I doubt the transformer is listed to be installed in this manner.
 

John120/240

Senior Member
Location
Olathe, Kansas
All the ones I've seen like this the transformer just sitting in there loose, no divider between voltages, and electrician saying "of course its all right, thats the way we've always done it":happysad::slaphead::blink:

Sounds pretty hack to me.
I doubt the transformer is listed to be installed in this manner.

Correct you both are. Yes That's the way it's always been done. Compliant or not it has never been an issue with AHJ.
 
Status
Not open for further replies.
Top