How are they getting the EGC to the UPS?Hi all,
I received this picture from a colleague asking if the installation is allowed. The plug feeds a UPS. I told him I'll dig more, but it will be nicer to install an outlet and plug the ups there.
View attachment 20355
My question is: is there a violation?
if yes, where does the code address it.
thanks,
qasim
How are they getting the EGC to the UPS?
300.3(B)
110.3(B)
Look at the color coding and the type of plug! (American) NEC has nothing to say about it!
But still a hack job IMO, and yes Grounding?
I would say it violates both a NEC article and the similar OSHA regulation.
NEC Art. 110.3(B) which states that listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
OSHA 1910.303(b)(2) states that listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
I doubt that breaker is labeled or listed for use as a receptacle.
our specifications are based on IEC.
NEC is used for unofficial references.