hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have 208V single phase 4160 kw tankless instant hot water heater. See below link. Should the breaker be sized 20A, 25A or 30A?
Storage type water heaters of 120 gallons or less are considered continuous loads for the purposes of sizing the branch circuit per 422.13. But that would not apply to the water heater in the OP.
Electric pool water heaters need to have OCPD not less than 125% of the nameplate-rated load, per 680.10. So if the water heater is used for that application, 25A would be the minimum.
Otherwise, I see no reason that 20A would not be the minimum.
Cheers, Wayne
Is that 4.160 kw? 4160000w/208v=20,000 ampsI have 208V single phase 4160 kw
20 x 1.25. I wouldn't want a full 20a load, continuous or not, on only a 20a circuit.How?