And I go back to this....
90.1 Purpose.(A) Practical Safeguarding. The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity.
So you interpret 90.1(A) as only applying to users of electricity, not to electricians when they are practicing the trade. I interpret it to apply to everyone in all circumstances. We can agree to disagree.
The stated purpose is fulfilled without any rule for using handle ties or three pole breakers. MWBCs present no hazard to anyone using them. The '08 code change moved beyond that purpose to safeguarding bozos working on them. Yea, that's what we need more rules geared toward guys like the fella in your example. Let's do all we can to keep them afloat in the trade.
Like it or not, there are a whole bunch of persons employed as electricians who
(1) don't understand the hazard of opening a shared neutral in a MWBC without removing voltage from all the ungrounded conductors in the MWBC.
(2) don't possess the mystical powers of figuring out all the ungrounded wires' OCPDs while standing at a pre-2008-rules panelboard. I still have not been shown a method that will reliably indicate that without me having to find outlets on each of the hot wires in the MWBC. I'll not even ask for a method of finding the common neutral conductor's termination at the panelboard.
With the 2014 rules I can just walk up to a panelboard and see by the grouped breakers (handle ties or common trip) and / or by the conductor grouping what conductors are in a MWBC.
I'm all for getting the bozos out of the trade. Then I would not have to worry so much about what I may find. I would like to see license testing that included a demonstration of manual skills, continuing education requirements at least for new code cycles, and periodic retesting. I would also like to see a scheme for complaints against licensed electricians that included retraining as an option, rather than the current -- keep your license or lose your license, since taking away a persons livelihood is a serious step (and only done under extreme conditions).
I worked for almost 2 years, to no avail, to get an electrician I worked with either dismissed or trained and certified as having attained the necessary skills not to endanger me with his non-Code compliant work. He was offered a free, work time 9 month course which he refused to take after doing very poorly on the entrance test. He, like I, was a military veteran, but he played the "Veteran" card to excuse all his screw ups. And the bosses took it, hook, line, and sinker. [He had skipped the requirements for sitting for the journeyman's test by playing the veteran's card and went to a cram school (we'll keep pounding the likely test answers into your head until you manage to pass).]
I used to bounce MWBC all over the panel, I didn't, and still don't see it as a problem.
You will need to excuse my extreme ignorance. I have never worked under an NEC version that did not require:
210.4 Multiwire Branch Circuits.
....
(B) Disconnecting Means.
Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
It has only been in effect for 3 code cycles, but I guess the "training wheels" are still a sore point for some.
You are free to question my intelligence, I won't be offended. I don't think it is much above average, if at all. I struggle with basic math, couldn't tell the first thing about the magic that makes electrical stuff work once the discussion moves beyond circuitry and wires, shoot man, I can't make a post without using spell check on words with more than five letters.
I can figure out which breakers I need to turn off when working on MWBCs. Depending on where I am working on the circuit I may only need to turn one breaker off and still keep me and any equipment safe. Stupid handle tie rule makes that impossible.
You have a good point, can we come up with a reliable scheme for handle ties that will normally turn off all the breakers tied with the tie and also allow a single breaker to be turned off while leaving the other(s) on. Come to think of it, if the handle tie was supported by a hinge at each end and was placed outside the breaker handles on the "ON" side you could operate it to turn them all off meeting 210.4(B). You could also operate a single breaker to the off position. This would not give you a method for turning them all on at the same time, but that is not required.
I don't question anybody's intelligence if they don't know which breakers to turn off just because they are not grouped. I do question their qualifications.
See above about reliable method.
I resent code mandated training wheels like 210.4(B). They weaken the quality of the trade rather than elevating the importance of education, training, and skill.