it still has to end up green or bare.Originally posted by benaround:
Sam,
As far as I know it can be any color you want!
Code reference please?Originally posted by jbwhite:
it still has to end up green or bare.Originally posted by benaround:
Sam,
As far as I know it can be any color you want!
In that case, don't your inspector try to use section 310.12. (B) applies to EGC's as we all know. (C) applies to diferentiating between the ungrounded conductors and grounded or grounding conductors. A GEC is not a grounding conductor, although the definition is easily misaplied to appear that way. A grounding conductor does in fact connect to a grounding electrode (as expressed in Article 100), however, it is used for the connection to supplementary electrodes, as discussed in 250.54. The conductor you speak of is not a "grounding conductor", it is a grounding electrode conductor. If it weren't you wouldbe violating section 250.24(A), which requires a grounding electrode conductor, not a "grounding conductor".Originally posted by physis:
I want to use some of your guys' posts to straighten this fool out.
I'm interested in convincing this "sorta" friend of mine that I can be right and an inspector can have his head up something. His world view dosn't seem to allow for this possibility.By Ryan:
In that case, don't your inspector try to use section 310.12. (B) applies to EGC's as we all know. (C) applies to diferentiating between the ungrounded conductors and grounded or grounding conductors. A GEC is not a grounding conductor, although the definition is easily misaplied to appear that way. A grounding conductor does in fact connect to a grounding electrode (as expressed in Article 100), however, it is used for the connection to supplementary electrodes, as discussed in 250.54. The conductor you speak of is not a "grounding conductor", it is a grounding electrode conductor. If it weren't you wouldbe violating section 250.24(A), which requires a grounding electrode conductor, not a "grounding conductor".