5-196 Log #385 NEC-P05 Final Action: Accept in Principle
( 250.119 )
________________________________________________________________
Submitter: Dan Leaf Rancho Santa Margarita, CA
Comment on Proposal No: 5-220
Recommendation: Revise last sentence:
Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall be used only as an equipment bonding conductor.
Exception: Grounding electrode conductors shall be permitted to be identified in accordance with this section.
Substantiation: Since this section encompasses individual covered conductors, they should be covered by the proposal. Many installers employ green covering, marking, or stripping for grounding electrode conductors, though not required or prohibited by present Code, which provides a degree of identification from circuit conductors, especially where installed with other conductors in the same raceway or enclosure. Though this section relates to equipment grounding (bonding) conductors the wording appears applicable as a general rule.
Panel Meeting Action: Accept in Principle
Revise 250.119 to read as follows:
?250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section. Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors.?
Sections 250.119(A), (B), and (C) to remain unchanged.
Panel Statement: This meets the submitters intent. The prohibition against the use of green for any conductor other than an EGC is too broad. It prohibits the use of green for all grounding conductors other than EGC, such as GEC, intersystem-bonding conductor, etc.
Number Eligible to Vote: 16
Ballot Results: Affirmative: 16