kwired
Electron manager
- Location
- NE Nebraska
Unless you can point out what you though you didn't miss, read 250.119, allows EGC's to be bare and doesn't mention any specific locations being excluded. Swimming pool sections do trump the general rules and I know there is some places in 517 and 547 as well that would require insulated conductors and also trump the general rules.any in-ground wiring requires insulated egc. did i miss something from nec ?
250.120(B) does put some restrictions on where you can run bare aluminum EGC's.