insulated groundindig electrode in steel flex

Status
Not open for further replies.

kevinnye

Member
my foreman told me i couldnt use any flex in my groundig electrode for transformer. i changed from emt to flex when i came off the wall probaly 3 ft. the code says i can go up to six feet in flex with listed fitting. and i used a grnd bushing.if this were true why do they sell flex covered ground for residential.please reference 1999nec or 2002 since I'm in California. thanx
 
Re: insulated groundindig electrode in steel flex

250.64
(E) Enclosures for Grounding Electrode Conductors Ferrous metal enclosures for grounding electrode conductors shall be electrically continuous from the point of attachment to cabinets or equipment to the grounding electrode and shall be securely fastened to the ground clamp or fitting. Nonferrous metal enclosures shall not be required to be electrically continuous. Ferrous metal enclosures that are not physically continuous from cabinets or equipment to the grounding electrode shall be made electrically continuous by bonding each end of the raceway or enclosure to the grounding electrode conductor. Bonding shall apply at each end and to all intervening ferrous raceways, boxes, and enclosures between the service equipment and the grounding electrode. The bonding jumper for a grounding electrode conductor raceway or cable armor shall be the same size as, or larger than, the required enclosed grounding electrode conductor. Where a raceway is used as protection for a grounding electrode conductor, the installation shall comply with the requirements of the appropriate raceway article.
 
Re: insulated groundindig electrode in steel flex

From 250.64(B) it shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor .
When I was giged for this I thought "cable armor" was FMC, But was told by members of this forum that FMC is not cable armor it is a raceway, and the wire installed in it is not a cable for it to be the armor for. Cable armor is the outer sheathing of a cable assembly like AC cable, MC cable, MI cable ETC...
And since FMC is not in the list of wiring methods from 250.64(B) then it is not allowed just because of the statement "it shall be in" in that section.

And by the way: Yes you can get single conductor AC cable, even if it doesn't seem like it is a cable because of only one conductor it is a UL listed cable. :D

[ November 23, 2005, 08:34 PM: Message edited by: hurk27 ]
 
Re: insulated groundindig electrode in steel flex

imho, you are mixing the rules of (B) and (E)..FMC is a metallic receway and (E) requires bonding of metallic raceways...
with that said, i'll bow out and let others speak.,.. you have my opinion.
 
Re: insulated groundindig electrode in steel flex

Augie,

I think Wayne's right. There is a specific list of allowable raceways, FMT didn't make the list. While (E) mentions metallic raceways, so does (B), only in a more specific manner. You have to enforce (B) even though (E) doesn't name names.

Rigid nonmetallic conduit is mentioned in (B). Although common sense would dictate that we don't need to bond non-conductive raceways, it's not a sin for (E) to only make mention of the metallic options. ;)
 
Re: insulated groundindig electrode in steel flex

agree, george.. sorry couldn't get my mind off the bonding issue
 
Re: insulated groundindig electrode in steel flex

so what i get out of that is iam right. in san diego where i aprenticed, you had to flex your connections to a transformer for seismic reasons and the inspector also said nothing now that im in a new county. it was just the general foremen.
 
Re: insulated groundindig electrode in steel flex

But what you missed is FMC (Flexible Metal Conduit) or (GreenField) is not allowed as that flexable connection, but AC single conductor cable is. 250.64(B) does not list FMC as one of the wireing methods allowed. FMC is a raceway, AC is a cable.
 
Re: insulated groundindig electrode in steel flex

it must be different in so cal because of vibration,earthquakes thank you for that reference i had been over looking
 
Re: insulated groundindig electrode in steel flex

i found thiat i could in fact use the , and are required to by the cec (california electric code) that foremen has since been replaced by me.thank you for your replys though.
 