the ocp is a 50I 2pole in the mdp.#6awg is feeding the outside subpanel witch has a 30I 2polegfi and a 2pole gfi 20I the subpanel acts as the disconect and the ocp the 30I is for the motor i forgot what the 20 amp is for
That makes the 6AWG portion a feeder. The branch circuit(s) is after the final overcurrent device.