Insulated vs. Bare Ground Wire Application
Bare ground conductors comprise the grounding system. In manufacturing and industrial environments, #2/0 and #4/0 bare soft drawn copper, referred to as grounding electrode conductors in the NEC, interconnect all the grounding electrodes (Ground rods & bars, structural steel, rebar, etc.) per NEC section 250.50.

Insulated #4/0 bare copper conductors usually are used for DCS and PLC control system isolated ground systems. The insulated conductor is tapped from a ground rod triad, and the triad connects the control system ground to the main plant grounding grid/system. This insulated conductor normally terminates on an isolated ground bar. Insulated #6 or #8 are connected from the isolated ground bar and routed to control panel isolated/instrument ground bars to minimize noise and interference. These connections would be similar to the way the grounded conductor or neutral is treated, or an isolated ground receptacle connection, where there is a dedicated insulated/isolated ground routed from the source.
Respectfully,
Christopher D. Staker, PE
Atlanta, Georgia
Bare ground conductors comprise the grounding system. In manufacturing and industrial environments, #2/0 and #4/0 bare soft drawn copper, referred to as grounding electrode conductors in the NEC, interconnect all the grounding electrodes (Ground rods & bars, structural steel, rebar, etc.) per NEC section 250.50.

Insulated #4/0 bare copper conductors usually are used for DCS and PLC control system isolated ground systems. The insulated conductor is tapped from a ground rod triad, and the triad connects the control system ground to the main plant grounding grid/system. This insulated conductor normally terminates on an isolated ground bar. Insulated #6 or #8 are connected from the isolated ground bar and routed to control panel isolated/instrument ground bars to minimize noise and interference. These connections would be similar to the way the grounded conductor or neutral is treated, or an isolated ground receptacle connection, where there is a dedicated insulated/isolated ground routed from the source.
Respectfully,
Christopher D. Staker, PE
Atlanta, Georgia