Hi Guys,
Are the non-conductive conduits, such as PVC, need to have a stated rating for maximum voltage withstand? I know they are not typically Meggered, just an application came up where this spec may be necessary.
Regards,
EE
 

paulengr

Senior Member
Hi Guys,
Are the non-conductive conduits, such as PVC, need to have a stated rating for maximum voltage withstand? I know they are not typically Meggered, just an application came up where this spec may be necessary.
Regards,
EE

I don’t recall any insulation rating so depending on fillers used insulation resistance can vary. When building some home made moisture sensors years ago (home made Megger) I found a log of so-called insulators weren’t very insulative. Unless it was say rubber blankets most weren’t very insulating.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I agree with Dave and I know POCO's use PVC for MV cables quite often.

Roger
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
... [A lot] of so-called insulators weren’t very insulative. ...
Many plastics, rubbers and other polymers are conductive, often deliberately so.
There are conductive shoes available for static-sensitive environments, and tires are conductive to drain away any static charge that might be on the vehicle body when you pull up to a filling station. (I can't think of a much worse place for a static-electricity spark than between an open filler neck and a gasoline-dispenser nozzle)
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Now I see why gas stations post signs prohibiting cellphone use, and pipe everything in GRC. Perhaps a properly bonded metallic conduit conducts static charge buildup before a critical mass charge can develop lighting strikes.

Static discharge in this dry California climate destroyed my phone chargers, until the carpet, polyester sheets, blankets, & bath robe was removed & replaced with natural fibers.

Nose bleeds also stopped shortly after removing most static sources, albeit a coincidence.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Dielectric strength is a way of measuring the ability of a material to insulate (block conduction) and is usually measured in kV per mm of thickness.

PVC, with added "plasticizers to make it flexible, is the insulation material used on a lot of LV building wire like THHN, and is also used in some MV wire. The minimum dielectric strength of PVC wire insulation is 10kV/mm, the maximum is 30kV/mm. Hard PVC (no plasticizers) as is used in conduit has the same minimum, but a higher maximum, 40kV/mm.

 