Thanks, I actually don't need a complete computer analysis, just need a rough idea by doing hand calculations. The first link above does not work, but the second link (
https://www.google.com/url?sa=t&rct=...LUg9Qiki3Pc7tg) is helpful. On the first page of this link there is a graph, which indicates the factor for 400 kV is 0.85, which means 400*0.85=340 kV. So if the 340 kV is less than the BIL of the transformer, then will the transformer be safe?
Also the cable between the breaker and transformer would attenuate the surge-intensity very quickly. This reduction in surge intensity would depend on the C, L, and length values. Does anybody know the formula to calculate that how much would be the attenuation of the surge intensity per foot of 3-phase single conductor cable?
It can be done with hand calcs
an equivilent ckt needs drawn
showing junctions: gis duct to cable, cable to xfmr prim, xfmr, xfmr to gis duct
the surge Z for each component needs calculated or estimated from tables
Surge Z = sqrt(L/C)
call the transient pulse the incident wave
for each junction the following needs calc'ed
coef reflection r = (z2-z1)/(z1+z2)
coef refraction/transmitted = 1+r
this will calc how much
incident x (1 + r) = passes thru
incident x r = reflected back on self (could add, could subtract)
for the times/distances we are concerned with dampening due to R is small and can be neglected
for the same reason a reflected wave may add to an incident increasing significantly the magnitude
with this the mag at each junction/component can be determined based on the initial pulse/transient
for switching use 2 x sqrt2 x Vll/sqrt3 for the incident magnitude
if you are doing this as a learning exercise go for it
if you are doing this for actual sizing/purchase consult with someone who is proficient in this
I am not, just a cub scout