Re: Insulation resistance test of 600 V rated cables
To: takaimf, Megger check of Cables, and what are acceptable readings. I am going to respond to the original person that started this question.
The question was, "How important is it to check the conductors after an installation." And I am going to add some more helpful information.
No. 1. After any pull of large cables, it is always recommended to have a starting base-line of the Meg-Ohm readings of the cables. Also, you should set a minimum of what is the acceptable readings that you will accept.
No. 2. What is an acceptable reading? I have two manuals from the Company that use to be the Biddle Megger Company, and then they were AVO company, but I do believe that they are called the Megger Company now.
The names of the manuals are: "Stitch in Time" The Compete Guide to Electrical Insulation Testing. Featuring Megger Insulation Testers.
The name of the other manual is "Getting Down To Earth".
On page 14 of the manual,"Stitch In Time" it states the following: INSULATION RESISTANCE SHOULD BE APPROXIMATELY ONE-MEGOHM FOR EACH 1000 VOLTS OF OPERATING VOLTAGE, WITH A MINIMUM VALUE OF ONE-MEGOHM. FOR EXAMPLE: A MOTOR RATED AT 2400 VOLTS SHOULD HAVE A MINIMUM INSULATION RESISTANCE OF 2.4 MEG-OHMS.
I am going to give you my opinion of this reading of 2.4 Meg-Ohms. That would not be acceptable to me on a original installation. I would want to see Infinity or a reading of 200 Meg-Ohms plus.
Also, on page 20 of this manual they recommend the following DC Test Voltage for AC Equipment.
For example, Equipment AC Rating of 440 to 550 Volts, you would use a DC Test Voltage of 500 to 1000 Volts.
I have never had a megger destroy cable with the proper testing voltage, but I have seen the Hy-Pot testing destroy the cable or equipment.
If anyone would like to receive the two manuals that I have just mentioned, please contact me via a private message and I will put you in contact with the Applications Engineer at the Megger Company and hopefully he would sent the two manuals to you.