interconnected smoke and co2

Status
Not open for further replies.

GerryB

Senior Member
The conductor that interconnects is low voltage. I recall a few years back at class the instructor saying you could run that wire independent of the line wires (like if you ran 2-wire and not 3.) Anyone know if that's true? Run a # 12 or 14 thhn, outside the romex or mc?
 
The conductor that interconnects is low voltage. I recall a few years back at class the instructor saying you could run that wire independent of the line wires (like if you ran 2-wire and not 3.) Anyone know if that's true? Run a # 12 or 14 thhn, outside the romex or mc?
So it is similar to 0-10 volt dimming I would think, and thhn is 600 volt insulation. Question might be how do you enter into a metal box if that is what you had.
 
I'm guessing you are talking about the interconnect wire on standard 120 volt smoke alarms.
I have never seen any marking on these alarms to indicate the interconnect is class 2 or other low energy power supply. That being the case a chapter 3 wiring method must be used. Single conductor THHN is not an approve wiring method by itself. It would need to be installed in a raceway.
 
I'm guessing you are talking about the interconnect wire on standard 120 volt smoke alarms.
I have never seen any marking on these alarms to indicate the interconnect is class 2 or other low energy power supply. That being the case a chapter 3 wiring method must be used. Single conductor THHN is not an approve wiring method by itself. It would need to be installed in a raceway.
Standard BRK or Kidde, I don't plan on doing this, it's just something I recall being said. The job is an open ceiling and easily corrected the right way.
 
Standard BRK or Kidde, I don't plan on doing this, it's just something I recall being said. The job is an open ceiling and easily corrected the right way.

I thought there was something out there that I didn't know about. Never done or seen it done with other than 14/3. You must have been talking to a hack especially since he should know that you can't run THHN by itself.

-Hal
 
I just removed some old Square D smoke alarms from my house. Had two cables, one for power and another for the interconnect. Two different circuits powered them.
 
I'm guessing you are talking about the interconnect wire on standard 120 volt smoke alarms.
I have never seen any marking on these alarms to indicate the interconnect is class 2 or other low energy power supply. That being the case a chapter 3 wiring method must be used. Single conductor THHN is not an approve wiring method by itself. It would need to be installed in a raceway.
I agree just because something operates at a low voltage doesn't automatically make it a class 2 control circuit. For one thing the other conductor of the circuit is common with one the power supply circuit conductors. If it had two interconnect conductors like jimport mentioned - maybe the chance of actually being marked as class 2 is greater.

I just removed some old Square D smoke alarms from my house. Had two cables, one for power and another for the interconnect. Two different circuits powered them.
 