Interesting GFCI problem

Lmtoland

New User
Location
Alabama
Occupation
Electrician
Was called by my sister to help with a situation she encountered when she moved in to a new (to her) house. She assumed that this would be a simple issue for me and I did as well,, at least at first.

House she moved in to is a 1950's era farm house. kitchen wiring appears to be original (cloth insulation, two wire, no EGC) but outlets have been updated to GFCI outlets. The house came with a propane range. She brought her refrigerator (about two years old) with her. The only outlet within reach of the refrigerator was the outlet in which the propane range was already plugged in to which is a standard NEMA 5-15 receptacle which is fed from the load side of a 5-20 GFCI receptacle on the other side of the kitchen. No EGC is supplied to the receptacle.

Propane range functioned normally prior to installing the fridge and caused no issues even when utilizing the electric ignitor. However, once the fridge was plugged in to the same receptacle the GFCI would trip, sometimes immediately, and sometimes after several minutes. This would occur regardless of whether or not the range was being actively used.

I verified that the range alone did not trip the GFCI. I then plugged in only the fridge and it alone did not trip the GFCI. Only when both were plugged in did the GFCI trip. Naturally one would assume that there was a small amount of leakage current from each device that when added together would surpass the threshold of the GFCI and cause a trip. However, upon thinking about it, I considered this unlikely since there was no EGC and the appliances sat upon a ceramic tile floor in a house built over a crawlspace.

So after staring at the situation for a while and thinking it over I realized that the propane line running to the range was uninterrupted copper pipe that ran from the range into the ground in the crawlspace and emerged from the ground near the propane tank. So now I knew that the range and the fridge were being "grounded" through the propane line that connected to the chassis of the range which was in turn bonded to the EGC in the range cord which then created a path to ground through the outlet ground for the fridge.

Based on a few hunches, I plugged the range into the receptacle normally and then used a grounding adapter to plug the fridge into the outlet as well so that the EGC in the fridge cord would no longer have continuity with the receptacle and therefore the "ground" provided through the propane line. Now the GFCI holds. I then took some measurements and this is where it really gets bizarre. The voltage between the fridge chassis and the "grounded" range chassis was 22V. I should also mention that the fridge was plugged into a 5-15 outlet (non-GFCI) at her previous house which she says she feels sure was grounded because the "grounded" LED on her surge protector she once used for the fridge used to stay lit.

Out of curiosity, I place the back of my hand on the range and touched the fridge with my elbow expecting to sense a shock. I did not feel anything. However, I did hear a very faint buzzing sound when I bridged the two appliances with my arm. I used a different multimeter to check the values from before and confirmed the 22V to ground on the fridge frame. However, this meter gave me a frequency reading (the other meter did not have that feature) of 2.4kHz !? I initially doubted that reading, but it would explain the buzzing sound and the fact that I didn't feel a shock.

So, thoughts? Ultimately, the kitchen is going to be rewired completely. But, what do you suspect is going on here? is the fridge defective? Will is trip a rewired GFCI circuit that has a EGC? Or is something going on here that is just outside my experience that maybe one of you has encountered?
 
There are several common violations there:
A refrigerator cannot be connected to a GFCI protected 3-prong outlet without an equipment ground, 250.114 requires a refrigerator to be connected to an equipment grounding conductor (EGG) in all cases.

250.104 requires the propane lines to be bonded, but allows the EGC to the stove provide the function.
However the stove has no EGC.
250.114 probably also applies to the a propane range so the best bet is to run a equipment ground to that receptacle using the method described in 250.130(C)
 
Out of curiosity, I place the back of my hand on the range and touched the fridge with my elbow expecting to sense a shock. I did not feel anything.
Interesting measure the leakage current.
May less than 0.1mA as op not feel anything
But he also say gfci tripping, so more than 5mA leakage current
How no shock?
 
There are several common violations there:
A refrigerator cannot be connected to a GFCI protected 3-prong outlet without an equipment ground, 250.114 requires a refrigerator to be connected to an equipment grounding conductor (EGG) in all cases.

250.104 requires the propane lines to be bonded, but allows the EGC to the stove provide the function.
However the stove has no EGC.
250.114 probably also applies to the a propane range so the best bet is to run a equipment ground to that receptacle using the method described in 250.130(C)
The house was built (and likely wired) in the 50s. There are no EGCs.

Replacing a 2 prong receptacle with a GFCI per 406.4(D) does not invoke 250.114…..or does it?
 
The house was built (and likely wired) in the 50s. There are no EGCs.

Replacing a 2 prong receptacle with a GFCI per 406.4(D) does not invoke 250.114…..or does it?
406.4(D) is great for old homes like that, often just a GFCI breaker, most things in dwelling are still two prong, except the kitchen and laundry room.
406.4(D) wont work for anything covered under 250.114, often the only enforced item is a fridge, freezer and washer then 250.114 requires a EGC.
 
406.4(D) is great for old homes like that, often just a GFCI breaker, most things in dwelling are still two prong, except the kitchen and laundry room.
406.4(D) wont work for anything covered under 250.114, often the only enforced item is a fridge, freezer and washer then 250.114 requires a EGC.
But the wiring was compliant when installed. What makes 250.114 retroactive? Is every old home in violation?
 
Replacing a 2 prong receptacle with a GFCI per 406.4(D) does not invoke 250.114…..or does it?
See Informational Note #2.
Informational Note No. 2:
See 250.114 for a list of a cord-and-plug-connected equipment or appliances that require an equipment grounding conductor.
I tried to get an exception in 250.114 for this application but CMP 5 rejected it with the comment that the product standards for the types of equipment listed in 250.114 requires a connection to an EGC unless the equipment is double insulated.
 
I'd be tempted to just properly ground the receptacle so 250.114 is met and not have it on a GFCI.
Yes, since 3-prong appliances cause 250.114 violations with old work, one solution is to keep existing devices in place, to avoid 406.4(D) remodel codes that require xFCI.

Adding an EGC per 250.130(C) does not change the device.
 