During a down day here at our plant we went to several existing motors to take megger readings as part of a motor trending PM plan we have just started.
On one particular 150hp 480V motor we noticded that the megger was giving us a reading of 0 on each phase to ground. We then went ahead and disconnected the feeders from the motor and megged the motor again. This time we got the expected high resistance satisfactory readings to ground.
We then proceeded to disconned the motor feeders from the starter and take megger readings on the cables. We found that it was actually the cables that were giving us the bad megger readings to begin with for each cable was reading 0ohm to ground.
With each cable reading 0 ohm to ground how are we not tripping any breakers or buring anything up with a ground fault? Since all three of these phases are reading 0 to ground I would expect this to be a bolted fault condition and trip something or see a problem somewhere but this motor continues to run.
We have gotten readings with several different meggers and they are the same. The feeder distance is probalby a couple hundred feed and are 500MCM cables. Has anyone ever seen this before?
On one particular 150hp 480V motor we noticded that the megger was giving us a reading of 0 on each phase to ground. We then went ahead and disconnected the feeders from the motor and megged the motor again. This time we got the expected high resistance satisfactory readings to ground.
We then proceeded to disconned the motor feeders from the starter and take megger readings on the cables. We found that it was actually the cables that were giving us the bad megger readings to begin with for each cable was reading 0ohm to ground.
With each cable reading 0 ohm to ground how are we not tripping any breakers or buring anything up with a ground fault? Since all three of these phases are reading 0 to ground I would expect this to be a bolted fault condition and trip something or see a problem somewhere but this motor continues to run.
We have gotten readings with several different meggers and they are the same. The feeder distance is probalby a couple hundred feed and are 500MCM cables. Has anyone ever seen this before?