I have a friend who has a unique scenario, I thought I would see what this group has to say. First, the house:
This is a 40's era house that has no EGC's run throughout the house. The main service has a GES that includes a copper water line per 250.52(A)(1) and two ground rods per (A)(5). At some point a previous owner had "upgraded" all the receptacles in the house to 3-prong without supplying any EGC's, and didn't add any GFCI protection. He wants to "add grounding" by connecting some of the receptacles to the copper water pipes throughout the house, where convenient. This house is not in my jurisdiction, but I was asked for my professional opinion.
First question, is this explicitly permitted by code? I said no, 250.130(C) does not list metallic waterpipes as one of the six options for the replacement of nongrounding receptacles. However, I got to thinking and (C)(1) says "Any accessible point on the grounding electrode system as described in 250.50" and 250.50 says "All grounding electrodes as described.... shall be bonded together to form the grounding electrode system."
The copper water pipes throughout the whole house are all bonded together, does that make them part of the GES? If so, could the copper pipes throughout the house serve as EGC's? Metallic water pipes are not listed in either 250.118 (A) Permitted or (B) Not Permitted. In other words, it's not permitted, but it's also not not permitted...
Second question. I told him that my recommended solution (code approved) to his problem would be per 406.4 (D)(2)(b/c), add some GFCI receptacles. He likes this idea and plans on doing so throughout the house. Here's where it get's interesting. One room of his house is his "music studio" and he's wondering if, in addition to providing GFCI protection, could he also connect to the copper pipes to provide the grounding connection he desires for noise reduction.
Thoughts?
Thanks!
This is a 40's era house that has no EGC's run throughout the house. The main service has a GES that includes a copper water line per 250.52(A)(1) and two ground rods per (A)(5). At some point a previous owner had "upgraded" all the receptacles in the house to 3-prong without supplying any EGC's, and didn't add any GFCI protection. He wants to "add grounding" by connecting some of the receptacles to the copper water pipes throughout the house, where convenient. This house is not in my jurisdiction, but I was asked for my professional opinion.
First question, is this explicitly permitted by code? I said no, 250.130(C) does not list metallic waterpipes as one of the six options for the replacement of nongrounding receptacles. However, I got to thinking and (C)(1) says "Any accessible point on the grounding electrode system as described in 250.50" and 250.50 says "All grounding electrodes as described.... shall be bonded together to form the grounding electrode system."
The copper water pipes throughout the whole house are all bonded together, does that make them part of the GES? If so, could the copper pipes throughout the house serve as EGC's? Metallic water pipes are not listed in either 250.118 (A) Permitted or (B) Not Permitted. In other words, it's not permitted, but it's also not not permitted...
Second question. I told him that my recommended solution (code approved) to his problem would be per 406.4 (D)(2)(b/c), add some GFCI receptacles. He likes this idea and plans on doing so throughout the house. Here's where it get's interesting. One room of his house is his "music studio" and he's wondering if, in addition to providing GFCI protection, could he also connect to the copper pipes to provide the grounding connection he desires for noise reduction.
Thoughts?
Thanks!