I was sent this afternoon a one line. Kinda interesting
I take it 400-4-1G means 4- 400 amp rated conductors and 1-G means one ground. Which tells me is a installers choice. For the two 3/0 on the Fedder from transfer 400 amp main breaker to 400 amp ML panle,ok. The EGC sizing is incorrect as they used #4 in each raceway. Which should be #3.
The one line showed what I do believe is an GEC and required by the city of Tulsa which there is none in the service disconnect (service rated transfer switch). Utility and load reversed at there respective termination points.
The one line showed a nema 1, I do believe this sets outside.

I will confirm.
One line shows an 1/0 ground from utility transformer to the meter and the transfer switch

. This is not a feeder set up. It is a utility feed. The power company here does not allow this. They used to years back from what I'm told and since said no way. Also in the pic there no EGC on the utility side as shown on one line.
Since the ran 500 mcm and used the round up rule the one line shows 400 not 380, unknown connected load. Maybe should have ran 600 mcm cu. However with a 125 KVA generator I would think 500 would be ok.
Just another day in or industry.