I went searching for some voltage drop information here based on the 2002 NEC.
Here is part of it.
Here is part of it.
" CALCULATIONS FOR VOLTAGE DROP OF A FEEDER, OR A BRANCH CIRCUIT ?
?Special Note? The FPN Notes in the NEC are considered to be advisory, only.
If you adhere to the NEC requirement considering voltage drop.
The NEC requires the conductor to be able to carry the load, as per Article 220 PARTS B & C & D for feeders, and as per Article 210-19 for branch circuit conductors. Article 220 parts B, C, & D, calculates the load on a conductor at 100% for a non- continuous load, and at 125% for continuous load
PERIOD.
The NEC speaks nothing about giving a break for consideration of a loss of power, due to a voltage drop, that decreases the current carrying capacity of the conductor used. Therefore the NEC expects a full amount of power, [voltage], at ?end of line?.
Therefore the NEC requires that there will be no voltage drop allowance at all. You will find in ARTICLE 90-4 in the NEC that ?judgment calls? are up to the Authority Having Jurisdiction. Therefore, the Authority Having Jurisdiction has the authority to allow the use of the FPN note speaking of 3% on a branch, or feeder, and with a total voltage drop of 5% on the feeder, and branch combined. This NEC FPN Note can be used as an allowance for you to use that is within the authority of his judgment. Otherwise the NEC flat says that the conductor must be able to carry the load as computed in Article 220.