Over looking the fact, It looks "Hack" and there are open KO's, What code section would you call to fail the box being nailed like that?
Good question. The photo in post #5 is code compliant.
Over looking the fact, It looks "Hack" and there are open KO's, What code section would you call to fail the box being nailed like that?
314.23 B 1
Nails and screws, where used as a fastening means, shall be attached by using brackets on the outside of the enclosure, or they shall pass through the interior within 6mm (1/4 in) of the back or ends of the enclosure. Screws shall not be permitted to pass through the box unless exposed threads in the box are protected using approved means to avid abrasion of conductor insulation.
(I admit that it is hard to tell just how far the nails are from the back of the box, but they look to me like they are about 1/2")
Good question. The photo in post #5 is code compliant.