Here's the key phrase
With respect to the interlock kit, the ones made by the panel manufacturers state that they are UL listed for use with the panel. However, not all of them have a bolt-down feature . I believe the Siemens interlock kits have a metal, clip-on frame that is slid over the top 2 breakers on each side of the panel making it impossible to remove the generator breaker unless you forcibly remove that clip-on device.
Now, the kits available from www.interlockkit.com have a similar lock-down feature but use a cable tie instead of a metal clip. All the inspectors in my area will not accept these kits for that reason claiming that the cable tie is not a reliable holding device. In addition they are not UL listed with the panel.
That's why the inspector is wrong.Where manual transfer equipment is used.............The user of the optional standby system shall be permitted to select the load connected to the system.
With respect to the interlock kit, the ones made by the panel manufacturers state that they are UL listed for use with the panel. However, not all of them have a bolt-down feature . I believe the Siemens interlock kits have a metal, clip-on frame that is slid over the top 2 breakers on each side of the panel making it impossible to remove the generator breaker unless you forcibly remove that clip-on device.
Now, the kits available from www.interlockkit.com have a similar lock-down feature but use a cable tie instead of a metal clip. All the inspectors in my area will not accept these kits for that reason claiming that the cable tie is not a reliable holding device. In addition they are not UL listed with the panel.