I have a 1KVA control transformer that has 240V primary and 120V secondary. My primary fusing is 10A class CC fuse. I can cycle power to the machine 4 or 5 times in a row without any issue, but on the 6 or 7th power cycle I blow the 10A fuse on the primary. 10A is the maximum size fuse I can go, and I find it hard to believe that a CC fuse sized at just under 250% cannot hold.
On the secondary of the transformer I have a GFCI receptacle and a 60W 24VDC power supply. The 1KVA is overkill for this, but it is standard. I know that the inrush on the transformer is going to be worse depending on where the 60Hz cycle is at when power is applied, and I am also kind of suspect of the GFCI's unique relationship with ground that most loads do not have.
The wiring all looks correct on this transformer, any ideas from what I described above could be causing me intermittent trips? Could spikes on the 240V power supply to the primary cause this?
On the secondary of the transformer I have a GFCI receptacle and a 60W 24VDC power supply. The 1KVA is overkill for this, but it is standard. I know that the inrush on the transformer is going to be worse depending on where the 60Hz cycle is at when power is applied, and I am also kind of suspect of the GFCI's unique relationship with ground that most loads do not have.